the information found in our forums, are from many sources, qualified and un qualified as is the nature of the internet, and as such you use this information at your own risk. No liability directly or indirectly will be accepted by aussiedistillers.com.au, administration, the mod team or their heirs, whatsoever.

Regards,

aussiedistiller team.

REX C100 PID

Postby Kimbo » Sun Apr 13, 2014 5:49 pm

Hey, any of you nice people know how to program one of these PID's to remain at a constant temp?
I don't know what I have done, but when my water gets to the set value the PID wont cycle on and off to maintain the temp. It just stays on and the water keeps heating :angry-banghead:
Kimbo
Lifetime Member
 
Posts: 5461
Images: 0
Joined: Fri Mar 18, 2011 6:33 pm
Location: Perf WA
equipment: 4" bubbler with a 6"inline thumper

Re: REX C100 PID

Postby punchy21 » Sun Apr 13, 2014 6:16 pm

I haven't used one if those before but it sounds like it maybe a setting issue? Have you changed any of the settings from factory?
punchy21
 
Posts: 619
Images: 0
Joined: Fri Nov 04, 2011 11:56 am
Location: South West
equipment: Modular 4" 4 plate Bubbler
6kW 50L Boiler

Re: REX C100 PID

Postby Linny » Sun Apr 13, 2014 6:21 pm

Yep , are you sure the thermo couple has access to your wash ( as in is it too far away ? )

Auto tuning does help with the ramping of the element , but you might want to look at your cycle (R) to 1 sec

http://www.mpja.com/download/rex-c100.pdf

EDIT: can you take a photo of the label on the side of the PID ? there are several different models .
Linny
 
Posts: 1147
Joined: Thu Oct 11, 2012 8:46 pm
Location: Newcastle NSW
equipment: 4 Plate 3" Glass Bubbler - 50L Boiler
50L BIAB Temp Controlled Mash Tun

3" Carter Head Soon to Come

Re: REX C100 PID

Postby Kimbo » Sun Apr 13, 2014 7:02 pm

Yeah mate, the TC is definitely working, as the PID is seeing what the temp is.
I will adjust the Settings and report back :handgestures-thumbupleft:
20140413_165428.jpg

20140413_163327.jpg
You do not have the required permissions to view the files attached to this post.
Kimbo
Lifetime Member
 
Posts: 5461
Images: 0
Joined: Fri Mar 18, 2011 6:33 pm
Location: Perf WA
equipment: 4" bubbler with a 6"inline thumper

Re: REX C100 PID

Postby Yummyrum » Sun Apr 13, 2014 7:10 pm

I hope you are not using it to control the element direct. ......Thinking fused contacts...
Hopefully you are using it to control an SSR with it an external power supply.
Yummyrum
 
Posts: 1897
Joined: Fri Dec 28, 2012 3:19 pm
Location: Near Coffs
equipment: Did use Still Spirits Reflux
Now use 50l Keg with Pot head for Rum and Neutral stripping runs on gas .
LM/VM head with 1m packed 2" on Still Spirits boiler for Neutrals.

Re: REX C100 PID

Postby Linny » Sun Apr 13, 2014 7:20 pm

that PID wont control a SSR , you have to modify it since the output is a relay (like the SSR) and not a 12vdc SSR like it should say

here is my mash tun viewtopic.php?f=12&t=4099&hilit=+mash+tun




Whats happening is there is a small 3amp RELAY inside , which is turning your external SSR to full on. It does work , i had to do it to mine
Linny
 
Posts: 1147
Joined: Thu Oct 11, 2012 8:46 pm
Location: Newcastle NSW
equipment: 4 Plate 3" Glass Bubbler - 50L Boiler
50L BIAB Temp Controlled Mash Tun

3" Carter Head Soon to Come

Re: REX C100 PID

Postby L'ambeq » Sun Apr 13, 2014 7:33 pm

Hello Kimbo,

plesase send a wiring diagram or pictures so that it is possible to look if it is an connecting issue....

After that it makes sense to ask for the settings!

The controller should do a very good job if everything is OK , 0,5 degrees close to the setpoint is possible!

We will see if we can realise that!

Best regards
L'ambeq
 
Posts: 8
Joined: Wed Jul 31, 2013 6:27 am
Location: Germany
equipment: Potstill with surrounding waterjacket, digital controlled PID, SSR, 1kW element, 4L and 10L

Re: REX C100 PID

Postby Kimbo » Sun Apr 13, 2014 7:37 pm

Yummyrum wrote:I hope you are not using it to control the element direct. ......Thinking fused contacts...
Hopefully you are using it to control an SSR with it an external power supply.

All good there mate :handgestures-thumbupleft:
Linny wrote:Yep , are you sure the thermo couple has access to your wash ( as in is it too far away ? )

Auto tuning does help with the ramping of the element , but you might want to look at your cycle (R) to 1 sec

Nup! still not stopping at temp :crying-blue:

punchy21 wrote:I haven't used one if those before but it sounds like it maybe a setting issue? Have you changed any of the settings from factory?

definatly, I changed heaps of things which I cant remember... but I thought I put it all back to the factory settings
Linny wrote:that PID wont control a SSR , you have to modify it since the output is a relay (like the SSR) and not a 12vdc SSR like it should say

Yep, did that too :handgestures-thumbupleft:
Kimbo
Lifetime Member
 
Posts: 5461
Images: 0
Joined: Fri Mar 18, 2011 6:33 pm
Location: Perf WA
equipment: 4" bubbler with a 6"inline thumper

Re: REX C100 PID

Postby Linny » Sun Apr 13, 2014 7:53 pm

So you have modded and removed the relay in the PID ? .... if so , do you have a schematic or mud map how its all wired up
Linny
 
Posts: 1147
Joined: Thu Oct 11, 2012 8:46 pm
Location: Newcastle NSW
equipment: 4 Plate 3" Glass Bubbler - 50L Boiler
50L BIAB Temp Controlled Mash Tun

3" Carter Head Soon to Come

Re: REX C100 PID

Postby punchy21 » Sun Apr 13, 2014 7:56 pm

As it is heating up, is it turning on and off? And when it reaches temp it just stays on?
punchy21
 
Posts: 619
Images: 0
Joined: Fri Nov 04, 2011 11:56 am
Location: South West
equipment: Modular 4" 4 plate Bubbler
6kW 50L Boiler

Re: REX C100 PID

Postby mickiboi » Sun Apr 13, 2014 8:17 pm

If its getting to temperature and then staying on it sounds like you have the control action set wrong. It should be on 100% until it reaches temperature and then it should start to pulse on and off to maintain temperature. You may have the controller set for cooling, not heating. Change setting SL6 and see if that helps. See this for more help http://www.fmfranklin.com.au/products/d ... 100set.pdf.
mickiboi
 
Posts: 55
Joined: Sun Feb 23, 2014 4:37 pm
Location: South Australia Adelaide
equipment: Alex25

Re: REX C100 PID

Postby punchy21 » Sun Apr 13, 2014 8:25 pm

I was thinking that too but wouldnt PID stay off if the temp is below set point?
punchy21
 
Posts: 619
Images: 0
Joined: Fri Nov 04, 2011 11:56 am
Location: South West
equipment: Modular 4" 4 plate Bubbler
6kW 50L Boiler

Re: REX C100 PID

Postby mickiboi » Sun Apr 13, 2014 9:11 pm

punchy21 wrote:I was thinking that too but wouldnt PID stay off if the temp is below set point?

Hey punchy.
Direct action means Increase in input = increase in output.
Reverse action means increase in input = decrease in output.

If temperature(PV) is below setpoint(SV) and its set to cooling the controller will pulse on and off and as it approaches setpoint it will pulse quicker and quicker. When it passes setpoint it will go on 100% as it has exceeded it cooling setpoint so maximum output is required.

If temperature is below setpoint and its set to heating the controller will be on 100% as maximum output is required and as it passes setpoint it will pulse on and off slower and slower until it maintains setpoint.

Hope this helps
mickiboi
 
Posts: 55
Joined: Sun Feb 23, 2014 4:37 pm
Location: South Australia Adelaide
equipment: Alex25

Re: REX C100 PID

Postby Kimbo » Sun Apr 13, 2014 9:27 pm

Linny wrote:So you have modded and removed the relay in the PID ? Yes.... if so , do you have a schematic or mud map how its all wired up

PID Wiring.jpg


mickiboi wrote:If its getting to temperature and then staying on it sounds like you have the control action set wrong. It should be on 100% until it reaches temperature and then it should start to pulse on and off to maintain temperature. You may have the controller set for cooling, not heating. Change setting SL6 and see if that helps.

It did this when I was fucking around with the SV.... and its set to heating.
punchy21 wrote:As it is heating up, is it turning on and off? And when it reaches temp it just stays on?

as above ;-)

mickiboi wrote:If temperature is below setpoint and its set to heating the controller will be on 100% as maximum output is required and as it passes setpoint it will pulse on and off slower and slower until it maintains setpoint.

Yes, this is exactly how it should be operating..... but its not :crying-blue:
I will go and record where all my settings are and post them ;-)
Thanks heaps guys :handgestures-thumbupleft:

Oh!... build pics to follow soon :mrgreen:
You do not have the required permissions to view the files attached to this post.
Kimbo
Lifetime Member
 
Posts: 5461
Images: 0
Joined: Fri Mar 18, 2011 6:33 pm
Location: Perf WA
equipment: 4" bubbler with a 6"inline thumper

Re: REX C100 PID

Postby Kimbo » Sun Apr 13, 2014 9:44 pm

OK, my notes thus far:
when i turned it on, it didnt cycle or or predict, it just went to full power.
When it got to temp, the PV flashes but continues on full power.
AL1= 50
AL2= 50
ARU= 0
P= 30
I= 240
d= 60
Ar= 25
r= 1
oH=2
SC= 0

SL1= 0000
SL2= 0000
SL3= 0000
SL4= 0010
SL5= 0010
SL6= 0001
SL7= 0001
SL8= 0000
SL9= 0000
SL10= 1001
SL11= 0000

I hope this helps :pray: :pray: :pray:
Kimbo
Lifetime Member
 
Posts: 5461
Images: 0
Joined: Fri Mar 18, 2011 6:33 pm
Location: Perf WA
equipment: 4" bubbler with a 6"inline thumper

Re: REX C100 PID

Postby Linny » Sun Apr 13, 2014 9:56 pm

silly question but what type of SSR are you using ,,,, -da or -va
Linny
 
Posts: 1147
Joined: Thu Oct 11, 2012 8:46 pm
Location: Newcastle NSW
equipment: 4 Plate 3" Glass Bubbler - 50L Boiler
50L BIAB Temp Controlled Mash Tun

3" Carter Head Soon to Come

Re: REX C100 PID

Postby punchy21 » Sun Apr 13, 2014 9:58 pm

I think micki might be onto it - you have SL6 set to reverse action: 0001

Change it to direct and see what happens, looks like 0000?
punchy21
 
Posts: 619
Images: 0
Joined: Fri Nov 04, 2011 11:56 am
Location: South West
equipment: Modular 4" 4 plate Bubbler
6kW 50L Boiler

Re: REX C100 PID

Postby Kimbo » Sun Apr 13, 2014 9:59 pm

Linny wrote:silly question but what type of SSR are you using ,,,, -da or -va

SSR-25 DA ;-)
Kimbo
Lifetime Member
 
Posts: 5461
Images: 0
Joined: Fri Mar 18, 2011 6:33 pm
Location: Perf WA
equipment: 4" bubbler with a 6"inline thumper

Re: REX C100 PID

Postby Linny » Sun Apr 13, 2014 10:02 pm

Has to be settings ,,, hardware seems fine
Linny
 
Posts: 1147
Joined: Thu Oct 11, 2012 8:46 pm
Location: Newcastle NSW
equipment: 4 Plate 3" Glass Bubbler - 50L Boiler
50L BIAB Temp Controlled Mash Tun

3" Carter Head Soon to Come

Re: REX C100 PID

Postby punchy21 » Sun Apr 13, 2014 10:04 pm

is this for a HERMS Kimbo??