Kimbo wrote:OK, my notes thus far:
when i turned it on, it didnt cycle or or predict, it just went to full power.
When it got to temp, the PV flashes but continues on full power.
AL1= 50 SET TO 100
AL2= 50 SET TO 100
ARU= 0 SET TO 1
P= 30 SET TO 5
I= 240 SET TO 60
d= 60 SET TO 15
Ar= 25
r= 1 SET TO 2
oH=2
SC= 0
SL1= 0000
SL2= 0000
SL3= 0000
SL4= 0010 SET 0000
SL5= 0010 SET 0000
SL6= 0001 SET 0011
SL7= 0001 SET 0000
SL8= 0000
SL9= 0000
SL10= 1001
SL11= 0000
I hope this helps :pray: :pray: :pray:
Try these settings. I only use Sestos PID controllers and never have any trouble. I checked these settings compared to what I normally use. I couldn't find what the SL8,SL9,SL10,SL11 settings were in any manuals so I cant help with those. I know setting SL10 has to do with run/stop/start of the controller. If this fails set your Integral and Derivative settings to 0. This turns the controller into a straight proportional output, see what happens.