I've just set the PID testing turning the shed light on.

A section for all electrical discussions, including controllers, elements, wiring diagrams & schematics.
Forum rules
By participating in this section you acknowledge you are aware of aussiedistiller,com.au forum rules, policies & disclaimer.
If you are not aware please go to the rules section "before" you continue in this area of our forums.

"you expressly agree to hold aussiedistiller.com.au, Administration and moderator team, harmless for any property damage, personal injury and/or death, or any other loss or damage that may result from your use of the information or service provided here in and through out our forums"

the information found in our forums, are from many sources, qualified and un qualified as is the nature of the internet, and as such you use this information at your own risk. No liability directly or indirectly will be accepted by aussiedistillers.com.au, administration, the mod team or their heirs, whatsoever.

Regards,

aussiedistiller team.

I've just set the PID testing turning the shed light on.

Postby pocket » Thu Jun 30, 2016 8:59 pm

Nice setup on many PID controllers to look at thanks for the threads gents.
Much reading still not in any rush here do it once do it right.
No images from me atm;
I've just set the PID up testing it turning the shed light on and off atm.
Just setting up my PID I Have one simple question i have at the moment.
Where would the best place for the thermo coupler on 4" FSD NEUTRALIZER?
I cant belive how easy this PID is and it will be a new dawn from my Gas Pig Rig to electric distilling.

Thanks for that still Mr & Mrs Mac Cheers. The Quality of the service and Product is outstanding.

Many months away from running this rig as much going on just a spare hour.
Thanks in advance.
Cheers Pocket
pocket
 
Posts: 29
Joined: Sun Feb 24, 2013 1:54 pm
equipment: 3" Colum SS reflux

Re: I've just set the PID testing turning the shed light on.

Postby Meatheadinc » Thu Jun 30, 2016 9:16 pm

All depends what yo are teying to acheive.?
In my mind use the PID to control water flow in the RC via solenoid valve or porportional valve
Again wate are you trying to acheive ?
Meatheadinc
 
Posts: 561
Joined: Thu Aug 29, 2013 9:00 pm
Location: Far North Coast NSW
equipment: 2" LM/VM on 30L boiler
4" FSD Neutraliser 50L boiler
4" carter head thump column
"Control Freak"- Semi Automation

Re: I've just set the PID testing turning the shed light on.

Postby bayshine » Thu Jun 30, 2016 9:17 pm

Sorry mate but you cannot run a still by an off/on controller like a PID :handgestures-thumbdown:
viewtopic.php?f=60&t=3241
This is the type of controller you need to run a still by as it work by turning the Volts down but still keeps the power on( bit like tuning a gas burner up or down for more or less heat)
A pid will just get to your set temp and just shut off, and your still will just stop running and there is no set temp for running a bubbler.
Pid is good for a mash tun where you want to keep the mash at a set temp.
I hope this helps :handgestures-thumbupleft:
bayshine
 
Posts: 873
Images: 0
Joined: Sat Mar 16, 2013 11:30 pm
Location: Turquoise coast dubbya aye
equipment: FSD 6 inch 5 plater block head On a FSD 100lt pro boiler
3” copper reducer bokka on a keg boiler

Re: I've just set the PID testing turning the shed light on.

Postby Meatheadinc » Thu Jun 30, 2016 9:23 pm

What PID are you using .. some have PWM
Meatheadinc
 
Posts: 561
Joined: Thu Aug 29, 2013 9:00 pm
Location: Far North Coast NSW
equipment: 2" LM/VM on 30L boiler
4" FSD Neutraliser 50L boiler
4" carter head thump column
"Control Freak"- Semi Automation

Re: I've just set the PID testing turning the shed light on.

Postby andybear » Thu Jun 30, 2016 9:28 pm

If you have a true pid controller you will have a proportional output. You may also have a switched output to do the lights like your doing but a pid normally is a massive overkill to be used to switch things on and off. A thermostat is best for on off control.
Get a pic of your unit up for us to have a look at. :handgestures-thumbupleft:
andybear
 
Posts: 208
Joined: Tue Jun 10, 2014 10:51 pm
Location: Melbourne, Western Suburbs Area.
equipment: T500 has been retired and the 4" glass bubbler, has been christened. With 50 litre inverted keg, two 2400watt elements, 100mm sight glass and 100mm column connection and 1/2" drain. And all resting on a hexagonal frame with lockable castor wheels.

Re: I've just set the PID testing turning the shed light on.

Postby pocket » Mon Jul 04, 2016 12:20 am

Thanks for the reply's
The Question is where to put the themo coupler on the still. More to the point this specific still head.
I am om obviously controlling the elements. (My Bad)
Cheers pocket
pocket
 
Posts: 29
Joined: Sun Feb 24, 2013 1:54 pm
equipment: 3" Colum SS reflux

Re: I've just set the PID testing turning the shed light on.

Postby pocket » Mon Jul 04, 2016 1:17 am

Meatheadinc wrote:What PID are you using .. some have PWM

Yer rito PWM signals? just a friendly question here.. :oops:
I am using REX-C100 PID with a 40 A SSR one for each element not going to get into your technical lingo as i said many moths away.
I may have the wrong thermocoupler +K Cable.
Do it once do it right.
I am not going to dive in and mess shit up so i will just get started now.
With a distilled water run.
Cheers Thanks for the reply
Pocket
pocket
 
Posts: 29
Joined: Sun Feb 24, 2013 1:54 pm
equipment: 3" Colum SS reflux

Re: I've just set the PID testing turning the shed light on.

Postby pocket » Mon Jul 04, 2016 1:22 am

andybear wrote:If you have a true pid controller you will have a proportional output. You may also have a switched output to do the lights like your doing but a pid normally is a massive overkill to be used to switch things on and off. A thermostat is best for on off control.
Get a pic of your unit up for us to have a look at. :handgestures-thumbupleft:

I've posted pics to soon here and got bagged so no images until i do the popper learning curve. hence the light in the shed. :oops:
Cheers
And Thanks for the reply Pocket
pocket
 
Posts: 29
Joined: Sun Feb 24, 2013 1:54 pm
equipment: 3" Colum SS reflux

Re: I've just set the PID testing turning the shed light on.

Postby hillzabilly » Mon Jul 04, 2016 1:31 am

If ya thinkin you can set the temp to 78.5'c and it will run like a reflux still I think you will be mistaken ,the neutraliser(a plate based still) is controlled by adjusting the coolant flow to ya RC to get the required output,being flow rate and %ABV indicated with the parrot and alcometer ,I had only had reflux stills(nixon stone desighn) befor I bought one and the golden rule with them is ta run it to a still head temp of 78.5'c , but what ya didnot have is those bubble plates ,wich require a different aproach,its the amount of refluxing liquid that makes them do the job not the still temp ,that should only be considered a guide,most just use 2 elements ta heat to it starts flowing ,then 1 is shut off and the adjustments made to RC coolant flow.Above the RC would be were thermos have been put on the neutraliser befor ,but only as a guide.just my opinion tho ,cheers hillzabilly ;-)
hillzabilly
 
Posts: 1509
Images: 0
Joined: Sun Jun 10, 2012 3:18 pm
Location: PERTH WEST AUSSIE
equipment: 10 gallon OZARK pot still ,2inch and 3inch Nixon Stone coloum stills ,10 and 18 gal beer keg boilers,5gal thumper keg.And the one and only 4" Five Star Southern Cross .

Re: I've just set the PID testing turning the shed light on.

Postby pocket » Mon Jul 04, 2016 9:24 pm

hillzabilly wrote:If ya thinkin you can set the temp to 78.5'c and it will run like a reflux still I think you will be mistaken ,the neutraliser(a plate based still) is controlled by adjusting the coolant flow to ya RC to get the required output,being flow rate and %ABV indicated with the parrot and alcometer ,I had only had reflux stills(nixon stone desighn) befor I bought one and the golden rule with them is ta run it to a still head temp of 78.5'c , but what ya didnot have is those bubble plates ,wich require a different aproach,its the amount of refluxing liquid that makes them do the job not the still temp ,that should only be considered a guide,most just use 2 elements ta heat to it starts flowing ,then 1 is shut off and the adjustments made to RC coolant flow.Above the RC would be were thermos have been put on the neutraliser befor ,but only as a guide.just my opinion tho ,cheers hillzabilly ;-)


Thanks great info Cheers
This will just be part of the project I haven't event thought of a boiler might save up for the 100 litre one in the store :music-deathmetal:
Cheers some images so far it took a while to find the right box will pit this to use on my old girl then.
Thanks Cheers Pocket
pocket
 
Posts: 29
Joined: Sun Feb 24, 2013 1:54 pm
equipment: 3" Colum SS reflux

Re: I've just set the PID testing turning the shed light on.

Postby pocket » Mon Jul 04, 2016 9:39 pm

Just begining


Just the story so far long way to go
You do not have the required permissions to view the files attached to this post.
pocket
 
Posts: 29
Joined: Sun Feb 24, 2013 1:54 pm
equipment: 3" Colum SS reflux

Re: I've just set the PID testing turning the shed light on.

Postby pocket » Sat Mar 03, 2018 12:55 pm

DSC05874.JPG

Just a quick Thank-you
Many Runs in now on the plated column.

Ive been an avid LPG User for my runs for many years now It worked for me.

I was reading a thread that Mac posted regarding home made element guards one thing lead to another
So now I'm converted to electric ^:)^
I thought i might share my version on a 2400 Watt Home made element guard

I started with my 1" Female x Female that I had added to my boilers.

I Tacked one on to the element then I lined the inside with a PVC Pipe.
Fitted a standard House tap outlet reducer ( Orange part) one end is 1" BSP and the reduced end was the right thread for my feral.
My mate wired them registered sparky and showed my test and tag man "both happy"

Cost Bellow
1" BSP Element $38
1" BSP Female x Female $2.74
Used other bits from around the shed

Thanks Cheers Pocket